Register 206 = Zero Export Power (target) on Deye SUN-5K-SG03LP1-EU #682
gonmag8
started this conversation in
Show and tell
Replies: 2 comments 2 replies
|
Point your AI agent at the docs and it should be able to build a custom sensor for you If this works we can add it to the library |
2 replies
|
Yes, drawing from the grid would probably have the same effect the problem in my case is that I spend about 10 months without drawing from the grid, I mainly use grid to sell electricity. One of the AI's have told me ( unsure if true) that this controller bug has been identified and corrected by Deye in the latest firmwares. |
0 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment

Uh oh!
There was an error while loading. Please reload this page.
Uh oh!
There was an error while loading. Please reload this page.
The reason I went looking for this is that I realized that sometimes my inverter zero export control goes very noisy and is oscillating +/-200w around zero (instead of staying stable at the 20W recommended by the manual).
On investigating this issue I have noticed that when this behaviour happens if I set Zero Export Power (target) to 100w wait 30 seconds and then set it back to 20w the controller stabilizes and is then happy at 20w.
Model: Turbo Energy (Deye rebrand) SUN-5K-SG03LP1-EU, single-phase hybrid, firmware confirmed on the SG03LP1 register set (matches single_phase.py / deye_sg03lp1 metric group).
Finding: Holding register 206 is the "Zero Export Power" setpoint shown on the inverter's own LCD menu — separate from register 245 (Max Sell Power). Neither single_phase.py nor kbialek/deye-inverter-mqtt's SG03LP1 docs currently list a register for this setting.
How it was found: Since it wasn't in the published maps, I polled a block of unused/undocumented holding registers (200–249, holding, U_WORD) with ESPHome's modbus_controller while changing "Zero Export Power" on the LCD to three different test values. Register 206 tracked all three changes exactly (raw value = watts, no scaling).
Register details:
Address: 206
Type: holding, U_WORD (unsigned — LCD does not allow negative values)
Range on this unit: 0–500 (min/max as shown on LCD; may vary by firmware/model size)
Scale: 1 (raw register value = Watts, no multiplier)
Write quirk: like most write registers on this model, it needs function code 0x10 (Write Multiple Registers) — in ESPHome that's use_write_multiple: true. Plain single-register writes (0x06) may be rejected depending on firmware.
ESPHome example:
yaml
use_write_multiple: true
modbus_controller_id: inverter
id: inverter_esphome_zero_export_power_target
name: "Zero Export Power Target"
address: 206
unit_of_measurement: W
value_type: U_WORD
min_value: 0
max_value: 500
step: 1
Thank you all for your work :)